How to simulate defects caused by GICs and network protection against this phenomenon
HYPERSIM simulates the impact of Geomagnetically Induced Currents (GICs) on power transmission networks and transformer saturation, enabling electromagnetic transient (EMT) and real-time analysis of geomagnetic disturbances (GMDs).
Key Simulation Capabilities & Modeling Principles
- GIC Excitation & Injection
Quasi-DC Voltage Modeling: A geomagnetic disturbance produces an electric field along transmission corridors. In HYPERSIM, this is modeled by placing series DC voltage sources along transmission line sections:
V
dc
=
E
×
L
(e.g.,
8
V/km
×
200
km
1600
V
).
Ground Return Paths: Quasi-DC currents flow through transformer neutral groundings and return through the earth below the line.
- Transformer Core Saturation & Network Effects
Half-Cycle DC Flux Offset: The DC current component shifts the operating point on the magnetization curve, driving the iron core into deep half-cycle saturation.
Harmonic Distortion: Saturated cores draw large, highly distorted, non-sinusoidal magnetizing currents that generate substantial voltage and current harmonics across the grid.
Reactive Power Absorption: Half-cycle saturation significantly elevates 50/60 Hz magnetizing current demand, leading to heavy reactive power consumption (e.g., hundreds of Mvars per bank), which can cause voltage depression or system instability.
- Core Geometry & Construction Dependency
HYPERSIM accurately distinguishes between different transformer core topologies:
Three Single-Phase Units: Extremely susceptible to GIC saturation because each phase provides a closed, low-reluctance iron path for DC flux.
Three-Limb Cores: Show much lower DC flux offsets and saturation because the zero-sequence DC flux is forced to return outside the core through the structural air and tank paths (high magnetic reluctance).
- Critical Transmission Line Modeling (Frequency-Dependent Lines)
GIC amplitudes depend heavily on accurate line and earth-return resistances at 0 Hz (DC).
HYPERSIM uses Frequency-Dependent Distributed Parameter Line (FD-DPL) models. Standard constant-parameter lines (evaluated at 50/60 Hz) erroneously apply AC zero-sequence ground-return resistances to DC currents, which artificially suppresses simulated GIC levels.