IEEE 123-Bus Stubline Compensation with ARTEMiS SSN in RT-LAB

Overview

An advanced RT-LAB / ARTEMiS example using the IEEE 123-node distribution feeder to demonstrate Compensated Stublines and SSN-based network decoupling for real-time simulation.

This advanced example demonstrates the IEEE 123-node distribution feeder using ARTEMiS Compensated Stublines and SSN. Four Compensated Stublines are used to replace selected pi-lines and decouple the complete circuit into three independent sets of equations, each solved with SSN.

The original pi-lines replaced by Compensated Stublines have lengths between approximately 700 and 1000 ft. The replacement stublines use a one-time-step propagation delay and preserve the same total inductance, which corresponds to an equivalent line length of roughly 14 km at a 50 µs simulation time step. The Compensated Stubline technique is used to minimize the error that would otherwise be introduced by the increased equivalent capacitance of the stubline model.

Key Features

    • Learning how Compensated Stublines can decouple a large distribution feeder for real-time simulation
    • Comparing native SPS solver behavior with ARTEMiS SSN using Compensated Stublines
    • Studying IEEE 123-node feeder behavior during a phase-to-phase fault at Bus 23
    • Understanding how SSN and stubline compensation improve scalability for larger electrical networks

Getting Started

    1. Open the IEEE 123-node feeder model and review the four Compensated Stubline locations.
    1. Identify how the circuit is split into three SSN-solved equation sets.
    1. Run the 50 µs test case and apply the phase-to-phase fault at Bus 23.
    1. Compare Bus 23 voltages/currents and main feeder currents against the native SPS nominal pi-line reference.

Model Specifications

Parameter Value
Product RT-LAB
Simulation type Real-time
Model version RT-LAB 2024.4+
Application Energy
Model file 123Feeder_Model.zip
Recommended time step 50 µs