Query on Signal Conversion Between Control and Network Domains

Hi Team,

I have a couple of questions regarding signal generation and signal-domain conversion in HYPERSIM.

Signal Conversion: Control Signal ↔ Network Signal

I would like to know whether HYPERSIM provides a dedicated block to convert:

A Control Signal to a Network Signal, and
A Network Signal to a Control Signal.

I explored the Control Signal Connector block, but it does not seem to address my use case.

Could you please advise if there is a specific block or recommended method for performing these conversions?

@RAVITEJA

Hi RAVITEJA,

You do not need a separate type-conversion block for this in HYPERSIM. The electrical network and control signals are handled as two different domains, so the conversion is done using physical interface blocks.

To bring a network quantity into the control domain, use a Voltage Measurement, Current Measurement, or Multimeter/Bus Measurement block. These measure voltage or current in the electrical network and output it as a numerical control signal, which you can then use in control loops, logic or maths blocks.

To send a control signal into the electrical network, use a Controlled Voltage Source or Controlled Current Source. The control signal acts as the reference input, and the source injects the corresponding voltage or current into the physical circuit.

The Control Signal Connector is only for routing or labelling signals within the control domain, similar to a Goto/From block. It cannot connect a control signal directly to the electrical network.

To help make sure you get the best setup, could you share a little more about your use case?

  1. What specific component or phenomenon are you modelling? For example, a grid-tied inverter, variable load/impedance, dynamic fault, or a custom controller interface?
  2. Are the control logic and electrical network running in the same task/core, or are you looking to decouple them across different time steps or computational cores?

The best interface and decoupling method can depend on what you are trying to exchange.

LET’S GO SORFINA !!!

This is amazing, thanks for being a community supporter

Hi Team,

Thanks for the quick response.

Regarding my application, as shown in the attached image, I am trying to measure the fault voltage from the network model and feed this signal into a UCM block, which expects a control signal input.

Since the measured fault voltage is available in the network domain and the UCM block operates in the control domain, I am looking for a suitable way to convert the signal between these two domains.

When I check whether the voltage measured and varc values, i see a zero value